The ball on plate problem consists of a flat plate on which a ball needs to be positioned. Ball positioning is only achieved through unstable equilibrium where any small changes in the plate angle will result in the continual acceleration of the ball until it leaves the plate. Such a system presents an interesting controls problem as closed loop control is needed for stable ball positioning on the plate.
A good approximation for controlling the ball’s motion is to decouple the x and y directions on the plate. This allows for two separate independent control loops. One loop controls the x-location of the ball and another controls the y-location. Each control loop for the x and y axis consists of two parts; an inner control loop and an outer loop. The inner loop is responsible for running the stepper motors in closed loop for angle control. Motor angle is obtained from quadrature encoders on each stepper motor. A set angle for the stepper motors is provided from the outer loop and the difference between the set angle and measured angle drives the stepper motor angular velocity.
The outer loop controls the actual ball position on the plate. The input to this loop is desired ball location and feedback is measured ball location. The ball location is obtained using a 4-wire resistive touch screen on which the ball rolls. The difference and rate of change of the difference between the set and measured locations determines the output angle that is fed into the inner control loop. The outer control loop takes on the form of a proportional-derivative (PD) controller, while all that is needed for the inner loop is a proportional controller.
The output from the entire control system is the position of the ball on the plate. The position is controlled by adjusting ball acceleration. Ball acceleration is a function of plate angle and plate angle is a function of stepper motor angle. Using the small angle approximation, a small change in motor angle from equilibrium should result in a linearly related change in plate angle and therefore change in acceleration of the ball. This rudimentary approximation works quite well for controlling the ball even at larger angles.
Supplies:
Step 1: ​Design Approach
The platform is designed to have three degrees of freedom. The stepper motors are set up in an equilateral triangle pattern. This configuration couples the x and y motion but results in a simpler mechanical design to fully restrain the platforms position. The design also allows the platform to pivot around the location of the ball instead of just the center. This approach should permit for more abrupt acceleration changes of the ball, as the ball goes through no vertical displacement during plate angle adjustments. Currently the platform is only programed to pivot about the center.
Closed loop stepper motors were chosen because they work with existing 3D printer electronics. Adding feedback eliminates the missed step problem inherent to stepper motors and allows for more accurate microstepping as the measured angle is controlled, not the step count.
Step 2: Materials and Tools
MATERIALS
  • 3" x 1/4" aluminum bar (2-3 ft)
  • 1/8" aluminum plate(enough to cut a 6" circle from)
  • 1/8" acrylic sheet (6" x 7.5" min.) and enough to cut three1/2" circles from
  • 1/2" aluminum round (about 6")
  • 9X Traxxas 5347 rod ends
  • 4.9mm OD X 2.8mm ID pultruded carbon fiber rod (about 10" worth)
  • Arduino Mega 2560
  • Ramps 1.4 3D printer control board
  • 3X DRV8825 stepper motor driver
  • 3X NEMA 14 stepper motors with minimum 26.0 OZ-in torque, 5mm double ended shaft
  • 3X US Digital E2-1000-197 quadrature encoders and method to attach to stepper motors
  • 8.4" 4-wire resistive touch screen and hardware to wire to microcontroller
  • quadrature encoder knob with push button
  • 12v minimum 4 amp DC power supply
  • 1-1/4" chrome steel ball
  • 9X m3-0.5 x 14mm socket cap screw
  • 6X countersunk screws to mount motors
  • 3X #6-32 x 7/16 in. socket cap screw
  • 6X #6-32 x 1/2 in. button head screw
  • 3X #8-32 x 1/2 in. socket cap screw and washers
  • #8-32 all thread or screws to use as all thread (about 12 in.)
  • #6-32 all thread or screws to use as all thread (about 2 in.)
  • wire for electronics
  • two part epoxy
  • double sided foam tape
  • thin double sided tape
TOOLS
  • CNC mill
  • manual lathe
  • drill press and bits
  • taps and drill bits for: #6-30, #8-32, m3-0.5
  • SAE and metric hex keys
  • screw drivers
  • electrical soldering supplies
  • computer with Arduino IDE installed
Step 3: Part Models
The included SolidWorks part models and drawing are for reference only. My intention is to provide enough detail for someone to make a similar project but not make an exact copy. One should improve on the design and adapt it to fit one's needs.
Step 4: CNC Mill 1/4 Inch Parts
Use the included SolidWorks models and reference drawing to generate machine code for the 1/4" bar. Parts were cut using a 1/8" two flute carbide endmill with a 1/2" depth of cut.
Step 5: CNC Mill 1/8 Inch Parts
Use the included SolidWorks models and reference drawing to generate machine code for the 1/8" aluminum plate and acrylic sheet. Parts were cut using a 1/8" two flute carbide endmill with a 1/2" depth of cut. A 1/8" engraving bit was used to cut the pattern on top of the acrylic sheet.
Step 6: Turn Inserts and Tubing
  • Cut 15 x 5/8" pieces of #8-32 all thread
  • Turn down 12 of the 15 pieces so 1/2 (5/16") of the piece slips inside of the carbon tube leaving the threads intact on the other half of the piece
  • Cut 3 x 5/8" pieces of #6-32 all thread
  • Cut 6 x 1" pieces of carbon tubing. These pieces should be as close in length as possible. I used the parting tool on the lathe.
Step 7: Turn Standoffs
  • Turn 6 pieces of 1/2" aluminum round to 1/2" long
  • Drill and tap (m3-0.5) one end of each piece to a depth of 1/4"
  • Chamfer the tapped end leaving a 0.2" diameter face
  • Reverse the part and drill/tap (#6-32) other end to a depth of 1/4"
Step 8: Drill Holes and Tap
  • Drill and tap the aluminum parts according to the provided drawing and solid models.
  • Before tapping the acrylic top sheet, glue the three small acrylic disks to the underside of the sheet aligned with the holes. Tap the holes in the acrylic after the glue is set.
  • Tap the Traxxas rod ends using a #8-32 tap.
Step 9: Assemble Frame
The first version of the motor arms and platform are shown while the finished project shows a revised set. The SolidWorks models for the revised parts are provided.
  • Attach the legs to the round 1/8" disk using the #6-32 button head screws.
  • Attach the standoffs to the motor arms using the #6-32 all thread pieces
  • Add the #6-32 socket head cap screws to the clamping end of the motor arms
  • Assemble the rod ends by pushing the balls into place
  • Attach the rod ends to the standoffs on the motor arms using the m3-0.5 screws
  • Attach the encoders to the backside of the stepper motors
  • Attach the stepper motors to the platform
  • Assemble the top triangular platform using m3-0.5 screws with the rod ends in place
  • Attach the arm Y pieces to the rod ends on the triangular platform using the 3 pieces of #8-32 all thread
  • Thread in the 12 pieces of #8-32 all thread into the arm Ys and remaining rod ends
  • Epoxy the 6 carbon tubes onto the threaded rods
  • After the epoxy is cured, slide the motor arms onto the stepper motor shafts and tighten the clamping screws
  • Fasten the top acrylic sheet to the triangular platform using 3 #8-32 x 1/2" socket cap screw
  • Adhere the touch screen to the acrylic sheet using thin double sided tape in the corners. Make sure the active side is up.
Step 10: Wire Electrical
The control electronics consist of easily obtained parts: an Arduino Mega 2560, RAMPS 1.4 3D printer control board and three DRV8825 stepper motor drivers. The three stepper motors will be labeled A, B, and C.
  • Attach the Arduino Mega to the underside of the assembly using foam double sided tape. Make sure contact between traces on the Arduino and the aluminum plate is not possible.
  • Modify two of the DRV8825 stepper motor drivers so that the STEP pin goes up instead of down. This will allow the pins to be connected to hardware timers on the Arduino.
  • Insert the RAMPS 1.4 control board into the Arduino board and DRV8825 drives into the X, Y, and Z sockets on the RAMPS board with the two modified drivers in the X and Y positions. The RAMPS should be set for 32 microsteps.
  • Connect stepper motor A to the X drive, motor B to the Y drive and motor C to the Z drive. If the motors spin the wrong direction when testing adjust the code or wiring.
  • Make the following pin connections:
    1. X driver step pin ----- D6
    2. Y driver step pin ---- D5
    3. motor A encoder a ----- D2
    4. motor A encoder b ----- D3
    5. motor B encoder a ----- D18
    6. motor B encoder b ----- D19
    7. motor C encoder a ----- D20
    8. motor C encoder b ----- D21
    9. 3X encoder +5V ----- +5V
    10. 3X encoder GND ----- GND
    11. touch screen X +5V ----- A12
    12. touch screen X GND ----- D44
    13. touch screen Y +5V ----- A10
    14. touch screen Y GND ----- A5
    15. quadrature knob a ----- D32
    16. quadrature knob b ----- D47
    17. quadrature knob button ----- D45
    18. quadrature knob GND ----- GND
  • The stepper motors are powered from 12V DC supplied to the outer power connectors on the RAMPS board
  • Removing diode D1 might be necessary if the Arduino 5V regulator overheats as was occurring on my board. The Arduino will need separate power if D1 is removed.
Step 11: 4 Wire Resistive Touch Screen
Ball location measurements are accomplished using an 8.4 in. 4-wire resistive a touch screen. Resistive
touch screens are effectively voltage dividers with the x and y locations measured sequentially. To obtain position from the screen, 4 microcontroller pins are required. All bins must be bidirectional with low output impedance and high input impedance. Two of the pins need to measure analog voltage. The top and bottom plates inside of the touch screen are resistive, in the range of 1K ohm, but insulated from each other when the screen is not touched. To make an X location measurement the two pins connected to the bottom portion of the screen are set to outputs with low impedance. One of the pins is set high and the other is set low. This creates an electrical potential across the bottom portion of the screen. The pins connected to the top portion of the screen are set as high impedance inputs and an analog value is recorded from one of the pins. When the screen is now touched, the top portion of the screen makes contact with the bottom, creating a voltage divider and producing an analog voltage proportional to the touch location in the X direction. The process is reversed to record the Y location of the touch.
It is desirable to only take measurement when a touch is present. A third configuration is set to wait for
a touch condition and only enter the location measurement state when a touch is present. This is accomplished by setting the top or bottom side of the screen to ground; setting the connected pins to output low. The other layer is connected to high impedance inputs with a pullup condition on one of the connected pins. The digital state of the pullup pin is monitored until a touch on the screen pulls the layer low by connecting to the other grounded layer.
Step 12: ​Control Methods
Stepper motors are normally operated in an absolute fashion where the amount of steps sent to the motor are tracked in order to determine motor movement. This procedure has two unwanted qualities. The most obvious is lost steps. If the motor encounters a load sufficient to stop motion, the actual position is lost, as the commanded steps no longer match the motors location. The less obvious problem is producing and counting motor steps when using microstepping at high speeds. A typical stepper motor has 200 steps for a full revolution. This translates to 6400 steps for a full revolution if using 32 microstep controllers. When running the motors at 300 RPMs, an output of 32000 steps per second are needed per motor. Running three motors would result in almost 200K logic changes per second. Doing this level of real-time processing on a 16MHz 8-bit microcontroller leaves no headroom for other tasks.
The solution is to offload the step generation to hardware level timers and compare registers while using encoders on the motors to directly measure movement. A closed loop system can then be setup with the input value representing the difference between a desired motor angle and the measured angle from the encoder. The output from the control loop would then set the motor’s RPM. The needed pulse train is generated from three 16-bit hardware timers with three compare registers. The timers are setup with no pre-scaling producing a count rate of 16MHz that resets when the count equals the compare register. A corresponding output pin is toggled on timer reset, generating a pulse train needed to move the stepper motor. The frequency of the pulse train is set by the size of the compare register and determines the RPM of the motor. Scaled output from the stepper motor control loop can now be fed into the compare register to set motor RPM. With this method, all stepper motor signal generation is accomplished at a hardware level leaving the microcontroller free for other tasks.
A proportional-derivative (PD) control loop is implemented in order to achieve staple ball positioning. An integral component was added, but not needed. The proportional term in the control loop is simply the difference between the commanded location and the measured ball location multiplied by a proportional gain. The proportional term results in smooth movement of the plate angle, as changes in ball location normally result in a large number. This is not true when calculating a simple first order derivative dx ≈ [x(i) − x(i−1)]/h as ball movement between measurements is small with relatively large noise. The behavior can be improved by increasing the time between measurements but then the system response time becomes large. The solution is to use more of the balls history to better predict the current velocity. A good approximation for the balls motion is constant acceleration as the plate’s angle is not rabidly changing. A second order accurate stencil using only past measurements to predict the current derivative is desired. The stencil should have good noise rejection and time response behavior. Pavel Holoborodko has published such a list of stencils for one sided derivative estimation from which a 16 point stencil was selected. The resulting derivative is significantly smoother than the simple case while maintaining good system response time.
Both proportional and derivative components are added together such that the proportional part tilts the plate to accelerate the ball toward the set location and the derivative component tilts the plate to slow the balls motion. The magnitude of each value can be set by adjusting the gain values until the system is critically damped.
Platform angles representing X and Y tilt need to be transformed into the three stepper motor angles. The X and Y axis are projected onto the three motor axis to determine relative control weightings. This approach is only an approximation of the desired behavior but works as needed.
Consistent code execution rates are needed. This is achieved through the use of an interrupt routine that triggers every 1ms off of Timer0. Code execution flags are activated in the interrupt routine that allow different portions of the code to run.
Step 13: Program and Tune Platform
The code requires several libraries including: encoder, running median, running average, and PID.
The PID library could be easily eliminated as only the proportional part is used for the stepper motor angle control.
The screen will need an initial calibration. In the beginning portion of the code under "touch screen stuff" calibration values can be entered. Uncomment "Serial.print(measured_x_pos)" and "Serial.println(measured_y_pos)" at the bottom of main loop to display the raw screen readings. Touch the screen at the indicted locations under the "touch screen stuff" section and enter the displayed values in the code. After calibration, re-comment the serial prints.
The quadrature control knob is used to adjust values during operation. The Arduino IDE serial monitor can be used to display the values. The first value displayed is the main control loop time in uS. This value should not exceed 5mS as that is the call interval of the main loop. The quadrature push button is used to advance to the next value. The next three values are the proportional, derivative, and integral gains. These values can be adjusted using the knob in order to achieve desired tuning. The ball should quickly move to the set location with minimum overshoot. The values will be lost during power cycle so they should be manually entered in code after tuning is complete. Offset values for the X and Y directions can be adjusted next. The ball will be offset from the desired position if the platform is not level and integral gain is not used. Change the offset values to center the ball on the platform when "0 pattern" is set. Different ball patterns can be selected with 8 patterns currently programed using parametric equations. The rate of ball movement is also adjusted with the "pattern rate" variable; smaller numbers equate to faster ball motion. The final value is "pattern direction" which sets the direction of ball movement.
The provided code is functional but still a work in progress. Feel free to make improvements and share.
Don't forget to have fun!
Sensors Contest 2016
Grand Prize in the
Robotics Contest 2016
First Prize in the
  • Arduino Contest 2019
  • Fandom Contest
    Fandom Contest
  • Woodworking Contest
    Woodworking Contest
126 Discussions
starholdens
Question 15 days ago
Hi
Many thanks for posting , amazing project. I have a few questions:
- Where in the code is the ppr for the encoder ?
- Do you have any code to run it using a AS5040 magnetic encoder instead ?
- Is it possible to run it without an encoder so remove the PID and set_angle = set_speed ?
Thanks
1 answer
271828-starholdens
Answer 10 days ago
-The PPR of the encoders is never directly set as it's never converted to an actual angle measurement. The encoders start counting when the control arms are in the lowest position with the motors off. The control loop uses the count directly therefore changing the encoder count will influence the tuning. The center position count is set in lines 242-244 as 450 and a max angle is limited to 900 counts in lines 254-265.
-I do not have any code for AS5040 but it should not be that hard to implement as there is a quadrature output and also an absolute digital output.
-You could run it without the encoders if the motors will not lose any steps. This would require larger motors than I'm using. The centering and angle limiting would also have to be changed.
There-isO
Question 4 weeks ago on Step 1
Hi,
I'm trying to program something similar. I have a couple of questions:
1. Why is it 3dof and not 2dof?
2. Can this be programmed with state space form?
3. Did you use Matlab and simulink?
Please advise at your earliest convenience.
Thank you,
-Damian
1 answer
271828-There-isO
Answer 4 weeks ago
1. You can control the ball's position with 2DOF, but I liked the geometry three motors provided. The three motors allow for no fixed pivot point and the potential to pivot about the current ball location.
2. Sure, it's a closed loop problem with inputs and outputs. It would probably work better as the the actual ball location can be accounted for.
3. Matlab/simulink was not used but would make coding much faster. GNU Octave would also work. Just need to set up the variables you want to send and receive from the microcontroller.
As a side not, if you are not interested in closed loop stepper motor control, I would recommend something like an RC servo.
NikolaT29
7 weeks ago
Can you please provide all the math you used for it and/or indicate the math techniques you used?
Like, I don't know what I need to do (in terms of math) to make motors move by keeping the ball in an specific position.
I did a fast review on your code, but I will take a long time to understand what it does as a whole. So I just want the maths to build my own code with an ATmega1284 and 3 servo motors.
hamza300
6 months ago on Step 3
Excuse me, I encountered a problem in the 3rd step: "Part Models" for the piece "arm.SLDA SM" who does not want to open in the solid works
can you send me the file (assemblage) in perfect condition?
Thank you"
271828-hamza300
Reply 6 months ago
The uploaded files are good. It looks like Instructables is renaming the parts when they are downloaded. They need to be renamed to match the originals.
IrwinL2
1 year ago
I wish to thank you for the tutoring for the 3DOF ball on plate project, I am building myself one like you did.
Thank you,
Irwin L.
IrwinL2271828-
Reply 6 months ago
hi, i was wondering what motor and encoder you recommend. the encoders you use are 100$ each. Thankx
271828-IrwinL2
Reply 6 months ago
The motors I used were surplus from eBay. I would try and find used or surplus motors with the encoders attached. The encoders should have similar resolution to the ones listed. You can use larger stepper motors if you modify the mounting.
IrwinL2271828-
Reply 6 months ago
OMRON E6B2-CWZ6C Rotary Encoder 1000P/R ?
will it work with this one?
271828-IrwinL2
Reply 6 months ago
That encoder provides the needed resolution but you would need to figure out how to mount it with the motors you select.
GabrieleB37
Question 6 months ago
Great project and execution! Was wondering where you purchased the resistive touch pad?
1 answer
MiguelC242
7 months ago
Help with the material and code,
cmego
10 months ago
I would like to pay for a prototype of this model, then I will do my own prototype. Hope someone can share a link in order to buy it. Best regards.
AndreaD20
Question 1 year ago
Hi, I really like your project! Could you please post the files as STL so we can use the 3D printer?
Regards,
1 answer
271828-AndreaD20
Answer 1 year ago
Thank you! I would not recommend 3D printing the original design as the parts are sized for CNCed aluminum. It would be much better to modified the design like dibloff did and size the motor mounts for the next size up. The larger motors will allow for much easier tuning as they will produce more torque.
dibloff
1 year ago
Ok. I was finally able to publish the video. You
can see it here: https://youtu.be/bmZijILO7dg
Unfortunately instructables uploaded the video
but it never published it. My 3D printed 3DOF is finally assembled. All
electrical seems to work well. Need to do the calibration but the serial port
gives me 6 digit output when I touch the screen. Also My screen might be
backwards. When I initially start it it’ll vibrate and wiggle tremendously,
then the rattling will die down. As far as it’s connected to the computer and I
only cut the steppers power when turning it on and off it’ll always come back
to the same position.
Edit 1: In the meantime I figured out the
screen calibration. My 8.4” screen axes are backwards relative to the original
layout. I think it works fine now. If I touch the screen off center it’ll lift
up that side, and I think that’s how it should be since the ball then will roll
towards the center.